1) do you get this error without the platform (load) or when connected to the gearbox or motor only
2) if connected to load what is your gearbox ratio and how much the platform weight
the reason i ask this is your motor is 0.5kw so i just thought your load is very important in this matter and like you said before your autotune with rotation is suppose to calculate motor inertia which may have something to do with current needed to turn motor and in turn moving the load
3) have u tried and do you get this error using V/F mode? because this is to rule out problem caused by auto-tuning and possibility that your motor parameter is falsified (deliberate or non deliberate, who knows). I have no doubt that the 6 wj200 is very good quality inverter.
4) can you post your motor parameter because i just learn that motor parameter is not the same for 380v in wye connection and 220v in delta connection? I ask for this in one of my thread but i can confirm this because my inverter supplier said the same
Clyevo:
1 - Errors occur when moving platform to setpoints. The higher the motor speed the higher the error rate. If I try VFD autotune in CT mode 'with motion' is causes an error. With lower voltages I can get auto tune with motion to complete rotations, but it ends in a fail indication. Static autotune at 220V will complete, and provide different motor parameters than default hitachi motor.
2 - 60:1. Platform is not connected during auto tune with motion. Resistance of rod ends and platform weight is minimal.
3 - I have not tried 'free V/F'. Also 'SLV' is not available in VT mode.
4 - I'm not understanding this question. I assume the value of any parameters detected with autotune would be dependent on the input voltage.
Riton:
Mine is a 3/4 HP @ 60hz (0.55kW)
Full load 2.6A @ 230V
VFD output V will be dependent on mains V. (should be 220 mains, motor accepts 190-230)
-Mitch
I have been reading the manual in your posts
This is my thoughts bases on my limited knowledge and i hope other members can add more
at the end of the day the most important thing to solve anything is to isolate the component that may cause the problem, in this case motor, inverter and even cables, and power supply stability
For inverter, determine whether it is SLV only problem or if V/F is can be used without acc/dec error
For motor, make sure the motor parameters input into the inverter is correct
For cables, make sure the running cable from inverter to motor is not too long and too wide (AWG below recommended) because can result in reduce voltage and thus higher current will be drawn into the motor to achieve the target torque
Your inverter is higher capacity than your motor so i think it is not the problem of your motor drawing too much current but more of the settings that regulated overcurrent protection which may be most possibly related by numerous settings in your inverter and most likely have something to do with the error you encounter during auto-tuning.
1- What error/ error codes did u get from this (i meant during auto tuning):
During auto-tuning set your acc/dec highest possible then you can change it back to tolerable settings afterwards. For deceleration you can reduce more after tuning if you install dc brake resistors.
2-
Your inverter WJ200-007sf is rated 1.1kw and 0.75kw for VT and CT respectively
I think you can only use CT mode, if according to this
This is quote from your manual:
So your nameplate/parameter for motor is :
rated power : 3/4 (1/2) or 0.55kw (0.4kw)
rated frequency is : 60hz (50hz)
rated voltage : 230V (190V)
rated current : 2.6A (2.2A)
rated speed : 1800 / 4 (1500 / 4)
If this parameter above is correct you can try this settings:
H003 to 0.4kw (your selection is ....0.2/0.4/0.75/1.5.....) -
there is no 0.55kw option*H004 to 4 pole
A003 to 50hz
A082 to 200v (your selection is 200v-400v) -
should be 190V according to your motor parameter (you can put V/F gain to 95)* so all your parameter should be based on 0.4kw, that will affect the parameter H33 Motor Constant IO (no-load current) which may have something to do with getting the over current during acc/dec
From your manual:
Unchanged is meaning they will use default hitachi motor values for H33 Motor Constant IO (no-load current)
So hopefully your rotation auto tuning would not fail to produce this parameter.
I think the parameters detected by autotune is unique to individual motor because the windings is different on rotor and stator so that resistance passing through it is different and thus current passing though it is also different. The inertia of the motor differ according to construction of the rotor and the load.
3-
Either you rotation auto tuning or only able to do static auto-tuning it is also important to adjust the motor constant base on your observation in your application (with load):
so you should set the torque limit to 106%
4-
However if your autotune fail static or rotation, can you post the history of error code pertaining to the autotuning session
Can you post the parameters generated by autotune here, especially curious is the H33 data (motor constant IO)